On a project, we had two small 480V chillers. The MCA for each was 41A. The service to the building was 208V, so we used a step-up transformer to obtain the 480V. I used an existing 112.5kVA step-up transformer thinking I would be OK. The chiller that showed up was a larger single chiller with a MCA of 141. The existing transformer can only handle 135A on the 480V side. The chiller is on a VFD and has two stages. I can't get the FLA from the chiller manufacturer. I think I'm on the ragged edge of using the 112.5kVA. Even though it's on a VFD, I'm concerned about being that close to the capacity of the transformer. Any transformer size recommendations would be appreciated. I'm a little out of my comfort zone since it's a step-up transformer and don't know if there are some traps that I need to avoid.
Thanks.
Mike
Thanks.
Mike