On a project, we had two small 480V chillers.  The MCA for each was 41A.  The service to the building was 208V, so we used a step-up transformer to obtain the 480V.  I used an existing 112.5kVA step-up transformer thinking I would be OK.  The chiller that showed up was a larger single chiller with a MCA of 141.  The existing transformer can only handle 135A on the 480V side.  The chiller is on a VFD and has two stages.  I can't get the FLA from the chiller manufacturer.  I think I'm on the ragged edge of using the 112.5kVA.  Even though it's on a VFD, I'm concerned about being that close to the capacity of the transformer.  Any transformer size recommendations would be appreciated.  I'm a little out of my comfort zone since it's a step-up transformer and don't know if there are some traps that I need to avoid.
Thanks.
Mike
	
		
			
		
		
	
				
			Thanks.
Mike
				