JoeStillman
Senior Member
- Location
- West Chester, PA
A 225 ton air-cooled chiller has 9 compressors and 12 fans. At 460V, the total RLA/FLA is 440 amps, or 351 kVA. The nameplate says the SCCR of its single-point-connection control panel is 5,000A.
Assuming a standard impedance of 5.75%, a transformer that is limited to 5,000A secondary fault current is around 230 kVA. So, the largest transformer that can feed my 351 kVA chiller is 230 kVA. Crazy enough yet? Just wait...
When I calculate the short circuit current on the chiller input bus, The worst case is a fault in one compressor and all the others running (i.e. contributing to the fault.) So the machine is pumping 2,800A into its own 5,000A control panel, leaving me with only 2,200A allowable from the upstream system.
My transformer has other loads on it, like a building with enough heat producing equipment to need two 225 ton chillers (did I mention there are two of these crazy things?) So I need a 2,000 kVA transformer to feed the load. With the transformer impedance and those pesky short cables, I'm only down to 25 kA at the chiller. Shall we put a line reactor ahead of the chiller to limit SC current? Sorry, if the reactor impedance is high enough to knock the fault-current down to 2,200 amps, it also knocks the operating voltage down to 380 volts. Ok then, let's look at current limiting fuses. Is there a current limiting fuse at 450A with a threshold below 5000A? Nope.
I contend that there is no power system in America that can feed one of these chillers within its SCCR. Why is this even a thing?
/rant
Assuming a standard impedance of 5.75%, a transformer that is limited to 5,000A secondary fault current is around 230 kVA. So, the largest transformer that can feed my 351 kVA chiller is 230 kVA. Crazy enough yet? Just wait...
When I calculate the short circuit current on the chiller input bus, The worst case is a fault in one compressor and all the others running (i.e. contributing to the fault.) So the machine is pumping 2,800A into its own 5,000A control panel, leaving me with only 2,200A allowable from the upstream system.
My transformer has other loads on it, like a building with enough heat producing equipment to need two 225 ton chillers (did I mention there are two of these crazy things?) So I need a 2,000 kVA transformer to feed the load. With the transformer impedance and those pesky short cables, I'm only down to 25 kA at the chiller. Shall we put a line reactor ahead of the chiller to limit SC current? Sorry, if the reactor impedance is high enough to knock the fault-current down to 2,200 amps, it also knocks the operating voltage down to 380 volts. Ok then, let's look at current limiting fuses. Is there a current limiting fuse at 450A with a threshold below 5000A? Nope.
I contend that there is no power system in America that can feed one of these chillers within its SCCR. Why is this even a thing?
/rant