And there's the problem with the specifiers not paying attention to Article 409. All it takes is basically the same amount of effort it takes to determine the correct interrupt rating of a switchboard or panelboard. In fact, at some point you will ALREADY have that information upstream of the equipment. So by simply using that value as the AFC and requiring an SCCR at that level, you guarantee that the control panel will not need anything more when it arrives. Sure, the actual AFC is going to be slightly lower by the time you get to the control panel terminals, but that isn't a problem.
Where the issue comes in with the equipment provider being cheap (and often just lazy) is that in order to get a higher SCCR rating, the panel builder becomes more restricted on what they can use in terms of components. It's fairly easy now to attain reasonable SCCR values, even relatively high ones like 65kA, by simply choosing power circuit components that have those higher values, or are UL listed in series combinations that attain them. That however generally means that you can't buy each separate component from the lowest bidder and end up using an ABB starter behind a Square D breaker, because why would ABB test their starters in series combo with a competitor's breaker? So what they do is just "kick the can down the road" to the hapless EC who has to deal with it in the field, where it's MUCH more difficult. They are only allowed to get away with that because nobody told them they couldn't. That's where the job specs come to play here.
Like Bob Peterson, when I was a panel builder, I too would choose to take the high road and inform my customers what I was giving them. But he's right in that if nobody addresses it up front ahead of time, purchasing agents and buyers are only going to look at the bottom line costs, so the "can kicker" wins, which all but forces anyone trying to compete with them to do the same. That's why it HAS to be addressed up front.
But sometimes the equipment is selected by HVAC guys and they figured out all the heating or cooling demands and what capacity of unit they need but know nothing about electrical other then they can order the unit in 208-230 or 460 volts.