Does anyone know what the Chinese equivalent of the NEC is? I have spent a bit of time searching for an answer and cannot.
Based on the investigations of Chinese made products by forum members, I'm guessing the answer is "Codes? Codes?! We don' need no steekin' codes!"Does anyone know what the Chinese equivalent of the NEC is? I have spent a bit of time searching for an answer and cannot.
Based on the investigations of Chinese made products by forum members...
My reply was based on the assumption that what is true in one case is likely true in the other. By no means certain, of course.It is a common fallacy that the building codes, like the NEC, apply to products being manufactured.
Is the OP about product or installation?
My reply was based on the assumption that what is true in one case is likely true in the other. By no means certain, of course.
If an installation doesn't comply with any of the elements of the various standards, I don't see how it will comply with any Frankencode, however constructed.As I recall, China has its own standards with elements from IEC, IEEE and other organizations. Having seen some installations there, it's difficult to determine to which standard(s) the installations were made.
I agree, however in the case of NFPA 70 it is the required minimum federally, so although a state, or local municipality may chose to implement additional standards or regulations you would be hard pressed to find one who gives you less strict requirements. NFPA 79 is meant to cover equipment which acceptations have been applied since additional safe guards are in place and at times it is ok to see electrical equipment fail. You will not see a UL listing on a piece of OEM equipment which has three control panels, and 40,000 pounds of stainless machinery attached, but you will see most of it adhere to NFPA 79, and when it doesn't someone will want to know how it is compliant. Most OEM's design to NFPA 79 standards since it was specifically tailored to situations outside the scope of a traditional install (much like a motor circuit has special allowances since by design it may incorperate overloads, VFD's, Soft starts, as well as circuit breakers). Additionally, NFPA 70E addresses safety beyond the scope of install. They are all meant to be different limbs of a single body. So although none of the codes are the one shot go to, in the situation I described, barring FDA requirements of 21 CFR 11, and the very broad terminology used by OSHA these would be the governing standards used in 99% of US applications. China seems to break theirs down into sections... one for lighting, one for rotating machines, one for cabling, etc. I was hoping that maybe there is a short list, or a compiled version that would lead me to the ones that govern "most" installs.I would assume there is no single 'code' in China, just like there is not just one in the US.
NFPA79 is for industrial equipment and, to my knowledge, is 100% voluntary across the US. Compliance is specification driven.
NFPA70 is for installation, but it is only legally applicable on a state by state basis. some state have given authority for its application to municipalities.
NFP79E is about safely interfacing with energized electrical equipment in workplaces. It is not really applicable to equipment installation.
I agree, however in the case of NFPA 70 it is the required minimum federally...
Isn't that called "ribbon"?I spent a month in china once back in the 90s. Among other quirks they used black tape with no adhesive and tied wires together instead of using wire nuts. They also used mostly underfloor trenchs to route wires. Just wires with sand around them. No conduit even where the wires came out of the floor into boxes.
Not much different than what I saw in mexico when I was there about the same time except their black tape had adhesive.
I agree with what you are saying, and in my everyday work I use UL508A panel shops. Panel shops are for a different scope than what NFPA 79 is. And my point on the NFPA 70 being minimum requirement here, is that some edition of it will be the minimum required. I was an electrician for almost 20 years before getting a degree in Electrical Engineering. I have seen several AHJ require more than the minimum, but never knowingly less. And in my current line of work designing automation systems there is a very popular acceptance for NFPA 79, even when coming from across sea. Working this industry for the last four years has opened my eyes to alot I never saw as an electrician or as a facilities guy. My current topic of discussion comes because may become engaged in a foreign contract. I am one of the persons responsible for reviewing scope of work legal documents for electrical installations and have to point to a minimum requirement for the contractors hired to do the installation over there. This is just my initial pass at looking into this and it may end up being more headache than its worth, but it is for a longstanding valued customer, so even if it is a break even case it is worth me looking into. The reason I ask here (no offense to anyone) is that working in the trenches with Electricians for most of my career my bet dollar is on them, or an OEM tech. for having come across this more likely than one of my current cohort. Also, my grandfather who passed a few years ago was a lifelong Master Electrician and an inspector for over 25 years when he set his tools down. He came on here from time to time and gave information freely. When I run into any odd ball circumstances I look to these kind of forums to point me in the direction which typically helps me find an answer.Each state is allowed to chose which edition of the NEC they want implemented in their jurisdictions. Some states do not even accept it all. My home state completely ignored the 2014 edition, instead jumping from 2011 all the way to 2017.
OEMs are certainly allowed nad may even be encouraged to design and build their equipment to NFPA79. Overall most of the small panel shops, that I have experience with, don't even own a copy. UL508A is definitely more common than NFPA79.
NFPA70E contains almost no useful information for general design and installation of systems. It simply provides a list of suggestions that should be followed in order to create Electrically Safe Work Practices based on what has already been installed. You are correct, it is often cited by OSHA and most companies follow it, but it is not a requirement. It does not contain any restrictions on electrical installations except for labels to be installed, it just says what to do based on those hazards which it helps identify. It leaves the risk analysis and acceptable hazard level choices up to the employer. For example, there is nothing in NFPA70E against having a system with more than 40 cal/cm^2 incident energy, even though it would be difficult to maintain and troubleshoot.
All of the above standards are optional, and therefore need to be specifically included in project specifications.
Now was your original post about, which standards might be employed somewhere in China, or was it for those required for a specific project or location?
Do you remember the name your grandfather used on this forum?..Also, my grandfather who passed a few years ago was a lifelong Master Electrician and an inspector for over 25 years when he set his tools down. He came on here from time to time and gave information freely.
I am one of the persons responsible for reviewing scope of work legal documents for electrical installations and have to point to a minimum requirement for the contractors hired to do the installation over there
With its strong central government and managed economy, I very much doubt that China would allow provinces or cities to set up their own electrical installation codes. But I cannot say that for sure.I would assume there is no single 'code' in China, just like there is not just one in the US.
NFPA79 is for industrial equipment and, to my knowledge, is 100% voluntary across the US. Compliance is specification driven.
NFPA70 is for installation, but it is only legally applicable on a state by state basis. some state have given authority for its application to municipalities.
NFP79E is about safely interfacing with energized electrical equipment in workplaces. It is not really applicable to equipment installation.
Over the years my observation about Chinese machine purchases is that they will buy from anyone. They don't really care what standard it is built to.With its strong central government and managed economy, I very much doubt that China would allow provinces or cities to set up their own electrical installation codes. But I cannot say that for sure.
As to enforcement and the possibility of inspectors looking the other way, there may well be regional differences.