Chint inverter specs

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
In the specs for a Chint CPS SCA60KTL-DO/US-480 it says "Max. apparent power (selectable) 60 / 66kVA" and "Max. output current @ 480 Vac 72.2 / 79.4A". I understand that this is because of adjustable power factor, but which current number should I use for OCPD and conductor sizing? My first take is that I should use the higher number to err on the conservative side. What say you?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Code simply calls for nameple max continuous output current, which I think is the higher number. Unless the lower current is part of a listed power control system, there's no code provision for using it.
 

ryangittens

Member
Location
usa
@ggunn I would argue that the nameplate would be based on the selction since it lists both options unless the inverter can change or override the selection automatically based on the loads.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
@ggunn I would argue that the nameplate would be based on the selction since it lists both options unless the inverter can change or override the selection automatically based on the loads.
I am not sure I agree with that. I will be using the higher number.
 