And yet another thread goes off into the weeds discussing oddball circumstances and details not germane to the original posting...
View attachment 15755
And yet another thread goes off into the weeds discussing oddball circumstances and details not germane to the original posting...
Threadjacking is always something to be wary of. In this case the OPs question was answered satisfactorily and the conversation continued on to other things. I don't see a problem.Ditto as this is not unusual.
The problem is if the instant element also in inverse breaker is fixed type (permitted by code), it may compromise motor protection.
So an instant and it are both unsuitable?
both are fine if code compliant
Even if fixed at 1700% or 578 A it will trip with a conservative i failt of 760 A
give a scenario with numbers that illustrates your concerns
Yep. You have a real world problem to solve right there. What do you think is the best solution?Considera 460Vac, 40 horsepower energy efficient motor with 52 FLA. A thermal magneticbreaker sized to 250% FLA is selected. Since a 130A (2.5 x52 = 130A) rating is not a standard ampere rating, a 150Afixed instantaneous breaker is selected. The actual instantaneouspick up is 2250 symmetrical rms amperes or 15 timesthe breaker ampere rating. This breaker will not respond instantaneously until a current of 2250 symmetrical rmsamperes or 3181 peak amperes flows. The 40 horsepowermotor’s first half cycle inrush is 629 peak amperes. So there will be no problem starting the motor, but a short circuitcurrent of, for example, 1900 amperes will not becleared until the thermal portion of the trip unit responds in, typically, several seconds. This may cause FURTHER damage due to delay in protective device operation.
Considera 460Vac, 40 horsepower energy efficient motor with 52 FLA. A thermal magnetic breaker sized to 250% FLA is selected. Since a 130A (2.5 x52 = 130A) rating is not a standard ampere rating, a 150A fixed instantaneous breaker is selected. The actual instantaneous pick up is 2250 symmetrical rms amperes or 15 timesthe breaker ampere rating. This breaker will not respond instantaneously until a current of 2250 symmetrical rmsamperes or 3181 peak amperes flows. The 40 horsepower motor’s first half cycle inrush is 629 peak amperes. So there will be no problem starting the motor, but a short circuit current of, for example, 1900 amperes will not be cleared until the thermal portion of the trip unit responds in, typically, several seconds. This may cause FURTHER damage due to delay in protective device operation.
An inverse breaker with adjustable instant element will do.Yep. You have a real world problem to solve right there. What do you think is the best solution?
Are you sure it will not trip on O/L?first I would choose a 125, not a 150, but let's use your 150
The 1900A short circuit current is a guess. It is possible with highhow was the 1900 fault i value derived? what location in the circuit?
the 2250 A / 1500% is too high
an Eaton Series C F Frame 150 A
at 1900 A (1900/150 = 1250%) min .008 max 0.025 sec, at 1500% it is in the mag/instant. region
the motor will not see 1900 if the fault is before it? it is shorted out of the fault path
even in you example not an issue
so what if the CB takes a few sec to trip?: the OL can handle it (see below), the conductor can handle it, and obviously the CB can handle it, and the motor is not involved
The inrush current of the 40 hp energy efficient motor in this case is more than 425A and so the breaker would trip.if an mag/instant only is used set at 800% ~425 A it will trip no issue
Further damage to life and other property, the faulted motor already needs replaced or rewound.To prevent further damage.
You have no idea.
If your panel is a typical "loadcenter" your only choices of breakers that fit it will all be inverse time breakers AFAIK.I've got to install a main breaker on a main panel for a 117A dwelling unit. I've doubts on which breaker should I install: an Inversed-time one or an Instantaneous-trip one.
At first, I decided to install a 125A inversed-time breaker by NEC 240.6, but I got confused if an instantaneous-trip should be use in this case. This is mainly because I yet don't know the characteristics that should be met in order to use any.
Which one do you think I should install?
Are you sure it will not trip on O/L?
The 1900A short circuit current is a guess. It is possible with high
system fault capacity and short to ground via motor core.
The inrush current of the 40 hp energy efficient motor in this case is more than 425A and so the breaker would trip.
Ingenieur:
I considered worst case scenario in post#25 and the Code does not prohibit the conditions mentioned in it. Thus the 150A inverse breaker with fixed instant element set at 15 times would operate only when the short circuit fault escalates to around 40 times motor FLA.