mkgrady
Senior Member
- Location
- Massachusetts
A church is looking to add AC. It has a 200 amp 120/240 service now. I'm trying to confirm the service is large enough. I looked at the electric demand over the last year from the POCO invoice and it peaked at 6KW (or 25 amps). That leaves 175 amps of head room. I'm thinking the load shouldn't exceed 80% of total. So I figure the total load at 240 should not be more than 160 amps. 160-25=135 amps. So the total additional load should not exceed 135 amps. Am I doing this calculation correctly?