Ken9876
Senior Member
- Location
- Jersey Shore
I need to add a circuit at this home, went there tonight. Circuit is for a 50 amp heat pump heater for a pool. There is a 3/4" conduit running from a outdoor meter/main with a panel to a pool sub panel 20' away, digging would be a problem because of the fancy landscaping in place. The existing circuit is a 30 amp 240volt. 4 #10 in pipe(RNC) now I want to add 2 #6 Thwn to this conduit. By my calcs. #10 = .0211sqin., #6=.0507 sqin. so I would use the existing # 10 grounding conductor and add 2 # 6 thwn's giving a total sqin of .1858, 3/4" is good for .203 sqin. With derating the 10's would still be good for 32 amps and the 6 for 60 amps. Anyone see anyproblems with this?