Been listening to MH’s NEC calculation stuff and very interesting.
Example I cam across on my drawings.
3P-100A fused switch in dist board that has 90A fuses is feeding AC unit with a 3P-100A unfused switch on it.
The FLA of the AC unit is 40A and the MCA is 50A.
Questions.
Example I cam across on my drawings.
3P-100A fused switch in dist board that has 90A fuses is feeding AC unit with a 3P-100A unfused switch on it.
The FLA of the AC unit is 40A and the MCA is 50A.
Questions.
- I’d think the AC unit would be a continuous load and multiplied by 125%. Seems like they did take that into consideration with MCA of 50A, correct?
- With the circuit ampacity being 50A I still need to have wire ampacity for at least 90A?