NEC 240.21 says "Overcurrent protection shall be provided in _EACH_ungrounded circuit conductor at the supply". Does this mean one wire one breaker, even if the breakers terminal and plate is made to accept two wires such as a SQ D 20 amp breaker with two slots in the plate for the wire to lay under.
 
Paul Bates said:
NEC 240.21 says "Overcurrent protection shall be provided in _EACH_ungrounded circuit conductor at the supply". Does this mean one wire one breaker, even if the breakers terminal and plate is made to accept two wires such as a SQ D 20 amp breaker with two slots in the plate for the wire to lay under.

No. if the breaker is listed for 2 wires then it is okay to have 2 wires under the screw. You don't need a breaker for each wire , you just need to have overcurrent protection on the wires. It is no different than one wire coming off the breaker and feeding 10 other wires in a JB. One breaker...
 
Paul Bates said:
NEC 240.21 says "Overcurrent protection shall be provided in _EACH_ungrounded circuit conductor at the supply".


Over current protection is over current protection just that. As long as the equipment is listed for that purpose.
 
Paul Bates said:
NEC 240.21 says "Overcurrent protection shall be provided in _EACH_ungrounded circuit conductor at the supply". Does this mean one wire one breaker, even if the breakers terminal and plate is made to accept two wires such as a SQ D 20 amp breaker with two slots in the plate for the wire to lay under.
No, 240.21 means that every ungrounded conductor requires OCP, not necessarily an individual one. The idea is to never have an unprotected hot wire.
 
Dennis Alwon said:
It is no different than one wire coming off the breaker and feeding 10 other wires in a JB. One breaker...


Dennis,good point I never thought of it this way...
 
Dennis Alwon said:
No. if the breaker is listed for 2 wires then it is okay to have 2 wires under the screw. You don't need a breaker for each wire , you just need to have overcurrent protection on the wires. It is no different than one wire coming off the breaker and feeding 10 other wires in a JB. One breaker...

The key word is CIRUIT conductor, not individual conductors. Careful wordsmithing on the part of NEC here. Kudos.....:wink:
 