Good guess iwire, but you are way off on this one.
That is called a secondary injection test set and is used to "simulate" the trip secondary current from the CT's to the trip unit. Typically most CT's on LVCB's have a XXXX:0.5A ratio so at full load the output of the CT is 0.5A. The secondary injection test set will simulate different load conditions (ex: 300% OL=1.5A) to trip the breaker, the time it takes to trip under a specific load is compared to the TCC for that trip unit. Secondary injection only tests the operation of the trip unit, trip coil, and tripping mech.
Seconday injection does not test the CT's which is why some companies/Orgs do not consider it an acceptable test, they require a primary injection test. Thats about a 2000Lb $100,000 test set that puts actual fault currents through the breaker.