D dahualin Senior Member Feb 5, 2008 #1 Does anybody have a spreadsheet to show the miximum wire size for different circuit breaker frame size? Sometimes wires cannot fit into circuit breaker's terminal because wire size increased for avoiding volt drop. Thanks.:-?
Does anybody have a spreadsheet to show the miximum wire size for different circuit breaker frame size? Sometimes wires cannot fit into circuit breaker's terminal because wire size increased for avoiding volt drop. Thanks.:-?
B bphgravity Senior Member Location Florida Feb 5, 2008 #2 This would be a specific detail per each manufacturer.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Feb 5, 2008 #3 Also, there have been threads about terminals designed for this very situation. They're basically crimp-on pins.
Also, there have been threads about terminals designed for this very situation. They're basically crimp-on pins.
iwire Moderator Staff member Location Massachusetts Feb 5, 2008 #4 Also many times you can order larger terminals for the breaker.