Re: Circuit breaker handle ties for line-to-line feed
Don,
I have reviewed the references again, and what I'm to understand here is that, even though the plotter is single phase 208v which may include only L-N loads or only a L-L load, or a combination thereof, that two individual 1P breakers tied together with a listed handle tie is approved.
Note the poster did not state whether or not the plotter required a neutral. If not the load must be L-L 208v. But assuming that it did the plotter has only L-N loads butr then again have a combination of both L-N an L-L loads.
If simply 120v L-N loads I would like to understand that it would be similar to where (2) 1p breakers with an approved handle tie must be used on home run circuit that lands on the same yoke.
If a combination of 120v and 208 loads wouldn't this be similar to a range or cloths dryer being supplied from a 1ph-3w, 120/240v source where a 2p common trip breaker must be used.
If simple a 208v L-L load wouldn't this be similar to supplying a 1ph-2w 240v A/C or water heater load which also requires a 2p common trip breaker?
I may be missing something here and I may not be seeing the forest through the trees but if the load consisted of all or part of a L-L 208v I would think that a common trip breaker should be applied here. I personally would like to clear both lines should one line overload or fault.
Thanks for your input.
Dave