I have a Villa with air conditioner split units and its ratings 5000 VA 1-Phase 220 V and 4000 VA 1-Phase 220 V and as per NEC 440-22 , The Proposed C.B rating as follow:
5000 VA , I= 5000/220 = 22.72 A and C.B Rating = 1.75 x 22.72 = 39.77 A , so we will use C.B Rating 40 A
4000 VA , I= 4000/220 = 18.18 A and C.B Rating = 1.75 x 18.18 = 31.81 A ,
so we will use C.B Rating 32 A
as per NEC , we use 175% and we can use 225% if the selected C.B is not sufficent for the starting current
My Q is : if i dont know the starting current for the Air Conditioner Split Unit
which factor must be used 175% or 225%.
Regards