ENDIX
Member
- Location
- balikpapan
based on NEC 240.4. C , state that the ampacity of the conductors shall be equal to or greater than the rating of the overcurrent device, that has rating 800 rated over.
is it mean that for current below 800 A, is allowed to use overcurrent device that greater than ampacity of the cable?? (except for cable size 10 AWG and smaller has state on 240.4 D)
thanks
is it mean that for current below 800 A, is allowed to use overcurrent device that greater than ampacity of the cable?? (except for cable size 10 AWG and smaller has state on 240.4 D)
thanks