I looked a job today where twelve GE circuit breakers are being used to control 120v florescent lighting in a warehouse. These breakers are worn and one has totally failed. If my understanding is correct, the only time a breaker can be used to control lighting is if they are marked for "switch duty" (SWD).
The owner is asking me to put in 12 toggle switches to control the lighting so he can avoid using the breakers. He specifically does not want a lighting contactor. There is plenty of room to do this near the surface-mounted panel, however I'm running up against the derating rules. If I run two short pieces of conduit with 12 conductors each (12 switch legs in, 12 out) to a switch box, I have to derate 50%. Since I want 20 amp circuits, I would have to run #10 which seems like a pain.
The switch box could be 6 4x4 deep boxes chase nippled together with 2 switches each. Or I could use two pole switches and switch two circuits at a time with less boxes.
An alternative I'm considering is mounting a 12 slot Cutler-Hammer subpanel with SWD breakers, but the same derating rules apply as far as I know. I can be a few inches away from the main panel.
Suggestions?
The owner is asking me to put in 12 toggle switches to control the lighting so he can avoid using the breakers. He specifically does not want a lighting contactor. There is plenty of room to do this near the surface-mounted panel, however I'm running up against the derating rules. If I run two short pieces of conduit with 12 conductors each (12 switch legs in, 12 out) to a switch box, I have to derate 50%. Since I want 20 amp circuits, I would have to run #10 which seems like a pain.
The switch box could be 6 4x4 deep boxes chase nippled together with 2 switches each. Or I could use two pole switches and switch two circuits at a time with less boxes.
An alternative I'm considering is mounting a 12 slot Cutler-Hammer subpanel with SWD breakers, but the same derating rules apply as far as I know. I can be a few inches away from the main panel.
Suggestions?