Re: Circuit Breakers
Originally posted by bphgravity: Would a L-L fault technically be a ground-fault? I always considered that a short-circuit. . . . what would be the proper used terminology for a L-L fault?
You are right, Bryan. An L-L is not a "ground fault."
At my desk I have a well-respected textbook by a well-respected author, and its subject is fault analysis. It names the four most common types of faults as follows:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Single Line to Ground Fault (SLG)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Line to Line Fault (L-L)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Double Line to Ground Fault (2LG)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">3 Phase Fault (3 ph)</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Quoting a Westinghouse resource, it states that the frequencies of these types of faults, as observed in transmission systems, are as follows:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">3 ph - 5%</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">2LG - 10%</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">L-L - 15%</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">SLG - 70%</font>
<font size="2" face="Verdana, Helvetica, sans-serif">