Circuit extension into laundry room from other room?

Status
Not open for further replies.

pfus

Member
Location
Chicago NW burbs
Occupation
Elect. Engineer
Goal:
- adding a outlet in laundry room on wall shared with powder room.

The situation:
- laundry room and power room share a wall.
- laundry room wall that is shared with power room has no outlet.
- laundry room has two outlets and one light - all on same dedicated circuit
- power room has a respectable on shared wall that would be ideal to tie into.

Question:
- does code prevent to extend an outlet into laundry room from other room on same circuit as long is it s clear it could not be used for washer/dryer? (opposite would not be )
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You said powder room, does this meet the definition of a bathroom? If so the bathroom receptacle circuit cannot supply a receptacle in the laundry room.
 

pfus

Member
Location
Chicago NW burbs
Occupation
Elect. Engineer
I should have thought about this before posting.

Currently, (to my surprise) the power room circuit actually drives
- power room light, exhaust, and one outlet
- one outlet in hallway
- laundry room light, exhaust, and one outlet (not washer/dryer).

I found this thread:
https://forums.mikeholt.com/threads/laundry-room-outlets.27475/
discussing a related topic without the powder room twist.


@480sparky : sorry, I was wrong. Laundry room circuit only drives dedicated washer/dryer outlet. Rest is from powder room.
Now, if powder room qualifies as bathroom this would be a violation....
 

pfus

Member
Location
Chicago NW burbs
Occupation
Elect. Engineer
I guess the resulting two key questions are:
- is a powder room a bathroom?
- can a laundry room contain an outlet from another circuit
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the Article 100 definition of a bathroom:

Bathroom. An area including a basin with one or more of the following: a toilet, a urinal, a tub, a shower, a bidet, or similar
plumbing fixtures.
 

tom baker

First Chief Moderator
Staff member
What this post is calling a laundry room, in the NEC its the laundry area. A bedroom with a washer-dryer is a laundry area. The code only requires at least one receptacle for the laundry area.
 

pfus

Member
Location
Chicago NW burbs
Occupation
Elect. Engineer
So, a powder room is a bathroom. Therefore, the circuit has to be dedicated and contained in this bathroom. That will require some rework in the laundry room. Laundry room light and fan need to be fed by other circuit.
 

tom baker

First Chief Moderator
Staff member
So, a powder room is a bathroom. Therefore, the circuit has to be dedicated and contained in this bathroom. That will require some rework in the laundry room. Laundry room light and fan need to be fed by other circuit.
There are two options for bathrooms.
1. 1 circuit for counter top receptacles only, can feed other countertop receptacles
2. One ckt for a bathroom, only one bath, nothing else.
 