Im working on a project for a local grocery store where they are replacing an existing RTU with a specialized RTU. The existing RTU is wired with 2/0 conductors and is equipped with a 175A circuit breaker. The NEW RTU is 177 MCA and the MOCP is listed as a 200A circuit breaker (FLA listed as 142).
The existing feeder between the electric room and RTU is pretty long and routed through exposed bar joists about 22' in the air. So basically, its going to be very expensive to replace in both material and labor even if the existing 2"conduit can be re-used.
Any suggestions to re-use the existing 2/0 conductors while still replacing the 200A circuit breaker to satisfy the manufacturer?
Screenshot of new RTU electric info is attached.
The existing feeder between the electric room and RTU is pretty long and routed through exposed bar joists about 22' in the air. So basically, its going to be very expensive to replace in both material and labor even if the existing 2"conduit can be re-used.
Any suggestions to re-use the existing 2/0 conductors while still replacing the 200A circuit breaker to satisfy the manufacturer?