What HEATER current ? FLA = 131.5
Hermetically sealed compressors have internal heaters
I would think that was in the rating
the few extra amps may be controls
What HEATER current ? FLA = 131.5
What HEATER current ? FLA = 131.5
topgone
MCA is Minimum cct amps ? no
RLA is Running load amps ? no
UL reference, you are stating the 177 (MCA) value /1.56 = normal operating amps ~ 114amp ?
Do you have a UL reference I can look this up ?
I am sorry, still not following you logic here
Your kVA number converts back to my ampacity that was stated as incorrect
I would leave the existing 2/0 there in a heartbeat.
I am sorry, still not following you logic here
Your kVA number converts back to my ampacity that was stated as incorrect
COMPRESSOR 1 59.32
COMPRESSOR 2 59.32
CONDENSER FAN1 7.0
CONDENSER FAN2 7.0
CONDENSER FAN3 7.0
SUPPLY FAN 16.7
Taking us back to the fla value on the nameplate is wrong and therefore the MCA is wrong which would end up making the 2/0 wire OK
Taking us back to the fla value on the nameplate is wrong and therefore the MCA is wrong which would end up making the 2/0 wire OK
Besides, HVAC manufacturers use do not put FLA of their compressors. They are using "rated load amperes" instead. RLA is a computed figure that manufacturers do to get UL listing; "the compressor manufacturer must run a series of tests to determine the Maximum Continuous Amps (MCA) before the overload trips. Once that has been determined, UL says to divide the MCA by 1.56 to determine the RLA."
Please have a copy of UL 1995. or download it here.
Please read Clause 36.12 Determination of Rating. Hope that helps.