Brother:
This is my addition to what the others have already said. I hope it helps.
Circuit breakers and fuses act as conductors while the circuit is under normal conditions.
Current flow conforms to Ohm's Law.
Fuses and breakers do not open instantaneously when they experience fault current through them. It takes a little while before they can open up to stop the current flow.
Fault currents also conform to Ohm's Law. The total impedance value must include all of the factors involved - the internal impedance of the source, impedance of service, feeders, etc. This fault curent can be extremely high due to the low impedance of short circuits.
The initial fault current through a breaker or fuse can be much greater than what the breaker or fuse is rated to trip at. For example, a 100 amp CB under fault conditions could have 8000 amps (arbitrarily chosen figure from me) flowing through it for a few cycles before the breaker trips.
And depending on the impedance of the total path, in other scenarios, that 100 amp CB could have 40,000 amps flowing through it until it trips open.
The interrupting rating of a CB or fuse is an indication of how much fault current the OCP can safely shut off.
If the Interrupting rating is exceeded in a fault, the OCP can be destroyed and can cause serious damage to persons and property. Like I said earlier, there are videos that show what can happen. The improper use of OCP Interrupting ratings can create a bomb!
There are formulas and tables which can be used to calculate the maximum fault available at the OCP device. They involve the source internal impedance, the voltage, the type of system, length of conductors, and type of wiring methods used.
These calcs aretypically made by enginners who specify the proper OCP while the job is in the planning stages.