If you go by 3watts / ft then a 1,000 foot bedroom would need more than 1 circuit
I agree but you are the only one who agrees with me on this one!!:lol:
210.11 Branch Circuits Required.
(B) Load Evenly Proportioned Among Branch Circuits.
Where the load is
calculated on the basis of volt-amperes
per square meter or per square foot, the wiring system up to
and including the branch-circuit panelboard(s) shall be provided
to serve not less than the calculated load. This load
shall be evenly proportioned among multioutlet branch circuits
within the panelboard(s). Branch-circuit overcurrent
devices and circuits shall be required to be installed only to
serve the connected load.