If fire ATS/controller was fed out of two power sources (normal utility and emergency generator) as allowed 695.B(2).
On normal source (utility power) the circuit protection shall be sized for locked motor current start ( or 6 X FLA )
On mergency source (gererator) the circuit protection shall be sized for regular motor start ( or 2.5 X FLA )
Is this correct? Just want to confirm, I am on the road now. Thanks!
On normal source (utility power) the circuit protection shall be sized for locked motor current start ( or 6 X FLA )
On mergency source (gererator) the circuit protection shall be sized for regular motor start ( or 2.5 X FLA )
Is this correct? Just want to confirm, I am on the road now. Thanks!