Cities that use conduit not Romex

Status
Not open for further replies.
NYC and most others have adopted the same life safety codes. No more than 6' Greenfield unless it's an existing wall cavity. No Romex, period. No non-metallic flex.

Sent from my XT1254 using Tapatalk
 
NYC and most others have adopted the same life safety codes. No more than 6' Greenfield unless it's an existing wall cavity. No Romex, period. No non-metallic flex.

Sent from my XT1254 using Tapatalk
So if you have a corrosive environment you are stuck with stainless raceways?

Is there a stainless steel liquid tight flexible metal conduit?
 
Minneapolis / St. Paul and many of the inner ring suburbs had a so-called "All Metal" code, regardless of occupancy, that described the allowed wiring methods. Any cable with a metal sheath and any metallic raceway method satisfied the All Metal Code.

The All Metal Code was instituted by electrical jurisdiction in the Thirties and removed in the Seventies.
 
Are you allowed to use MC/FMC?
I believe you are permitted but only for short runs in an existing installation (like adding a paddle fan to an existing bedroom) . If walls and ceilings are open you'll have to run new conduits or extend the existing conduit system (don_resqcapt19 please correct me if I'm wrong).
 