Section 250-6(b) and (c), NEC – 1999, also states:
“(b) Alterations to Stop Objectionable Current. If the
use of multiple grounding connections results in an
objectionable flow of current, one or more of the following
alterations shall be permitted to be made, provided that the
requirements of Section 250-2(d) are met.
“Discontinue one or more but not all of such grounding
connections.
“Change the locations of the grounding connections.
“Interrupt the continuity of the conductor or conductive path
interconnecting the grounding connections.
“Take other suitable remedial action satisfactory to the
authority having jurisdiction.