How do you guys interpret this ckt
To me it's #8 on a 55a breaker
15a for motor +40a for heater
Sent from my SM-G965U using Tapatalk
Even if it did need to feeds could I supply it with one and then put two ocpd at the unit
Sent from my SM-G965U using Tapatalk
I'm confused, it says an MCA and a MaxOCPD why would this be anything more than a single 40 amp circuit?
Looks to me like it gives MCA and MOCP for the heat and for the motor (separately)
No, but I agree with Augie, many units have both single and combined circuit ratings/markings, this one seems to have single circuit ratings only. Why, IDK?It's no different than an AC unit.
I'm using fmc (greenfeild) and thhn the problem is I priced and speced the job for a unit
Then when they arrived the unit was completely different (wish I had a $$ for every time that happened)so now I'm trying to utilize the existing conduit I already ran and just adding one more as opposed to completely redoing it.
So if I can I would like to run a feeder rated at 55 amps into a junction box and from that junction box tap to disconnects one rated for 40 and one rated for 15
Sent from my SM-G965U using Tapatalk
Nothing wrong with feeder taps either, feeder only needs to be 40 amps in this case.I see no problem with that