Not even to protect it where it enters the box? Every other cable and conductor get clamped?
Not sure what you are trying to protect it from?
Surface mounted meter/main panel, with the GEC run through the small 1/4" hole in the bottom and strapped to the wall surface.
FWIW... I use a 3/8 NM connector...![]()
Wow, you are good, I need a larger hole to do that.![]()
Where exposed, a grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage. A 6 AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; otherwise, it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Grounding electrode conductors smaller than 6 AWG shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor.Not even to protect it where it enters the box? Every other cable and conductor get clamped?
Surface mounted meter/main panel, with the GEC run through the small 1/4" hole in the bottom and strapped to the wall surface. What code sections would you quote to not allow this?
Thanks
IMO that is what the hole is for. Every service I ever installed was done using the 1/4" hole for the gec
Then why does the hole need to be punched.Im going out on a limb here, but I would think it was for water drainage, no?
Im not following? All the meters i've installed come with a 1/4" hole and a 1/2" ko....
The small hole is not open from the factory. You must knock out the hole to install the gec. If it were a weep hole I think it would be left out.
I think the gap around the covers is larger than the KO (for water to run out/under).
I am asking because, "good trade practice" would be to clamp the wire and several AHJs in my area require it, I stuck my neck out and asked an electrician to clamp the GEC #4 today (he was fine with it) but I want to be 100%, if I am asking for it, that I can justify the request. I just want to be fair.