Clamping bare #4 exiting service panel to water pipe

Status
Not open for further replies.
I think the gap around the covers is larger than the KO (for water to run out/under).:D

I am asking because, "good trade practice" would be to clamp the wire and several AHJs in my area require it, I stuck my neck out and asked an electrician to clamp the GEC #4 today (he was fine with it) but I want to be 100%, if I am asking for it, that I can justify the request. I just want to be fair.

IMO, fair would be providing a code article that was violated and then asking. :)
 
The common code section used (and the most subjective) is 300.4, but this is an easy arguement to get into. Like I said previously, most AHJ's in my area are calling this and there are over 15 separate AHJ's in a 40 mile circle.
 
The common code section used (and the most subjective) is 300.4, but this is an easy arguement to get into. Like I said previously, most AHJ's in my area are calling this and there are over 15 separate AHJ's in a 40 mile circle.

Just curious, what specifically in 300.4 would you cite?
 
I think the gap around the covers is larger than the KO (for water to run out/under).:D

I am asking because, "good trade practice" would be to clamp the wire and several AHJs in my area require it, I stuck my neck out and asked an electrician to clamp the GEC #4 today (he was fine with it) but I want to be 100%, if I am asking for it, that I can justify the request. I just want to be fair.

There is often gap around covers, and there is usually "weep holes" in bottom corners of any 3R enclosure, the 1/4 inch hole in question here has to be punched out to use it for any purpose. You have a better suggestion for its purpose other than GEC entries?

IMO, fair would be providing a code article that was violated and then asking. :)

Sounds fair to me:)

The common code section used (and the most subjective) is 300.4, but this is an easy arguement to get into. Like I said previously, most AHJ's in my area are calling this and there are over 15 separate AHJ's in a 40 mile circle.
Just curious, what specifically in 300.4 would you cite?
300.4 has nothing to do with securing a conductor, cable, raceway, etc to an enclosure. The title is "300.4 Protection Against Physical Damage."
 
The common code section used (and the most subjective) is 300.4, but this is an easy arguement to get into. Like I said previously, most AHJ's in my area are calling this and there are over 15 separate AHJ's in a 40 mile circle.

I have seen manufacturers cut sheets indicating that the small hole was in fact for the GEC
 
I think it was a Square D drawing, but I am not sure, that showed the 1/4" KO for use with the GEC.

I think you are correct only it is a 5/16" hole

ry%3D480
 