How many clamps are allowed on a ground Rod??
per-250.70 (2011) you are allowed one per ground rod, I have one with 3, and
the company would like to install another one on the same rod, should I just drive another ground rod into the ground?? see picture.
any and all information, Thank you.


1590536765639.png
reyamkram.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Wouldn’t an intersystem bonding connector work better?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
250.70 does not say only one clamp on a ground rod. It says one grounding electrode conductor per clamp, unless the clamp is listed for more than one conductor.
 

jap

Senior Member
Occupation
Electrician
The Master I apprenticed under would have had a field day with me if I had terminated the wire type GEC's pointed up like in the picture instead of down towards the earth.... just sayin. :)

JAP>
 

jusme123

Senior Member
Location
NY
Occupation
JW
Why not run one wire from ground rod and mount a ground plate on the wall