I'm trying to clarify a long-running debate regarding 220.14(I) and its applicability to dwelling units.
From what I understand, 220.14(J) covers receptacles specifically required by 210.52—namely general-use, small appliance, and laundry receptacles. Those loads are accounted for under the general lighting load using the 3 VA/ft² calculation.
However, optional receptacles—like those in an attic, workshop, bar area, or unfinished basement—aren’t required by 210.52. If that’s the case, wouldn’t they fall back under 220.14(I) and be calculated at 180 VA per yoke?
Some claim that 180 VA never applies in a dwelling, and that all 15A/20A general-use receptacle loads are included in the 3 VA/ft² calc, regardless of location or requirement. But I can’t find a section in the NEC that says 220.14(I) is completely excluded from all dwelling unit receptacles. In fact, 220.14(I) starts with “except as covered in (J),” which suggests it does apply to any receptacle not explicitly covered by (J).
So my questions are:
1. Are there any official references, CMP notes, or Handbook excerpts that clearly explain whether 180 VA per yoke should or should not apply to optional receptacles in dwellings?
2. If 220.14(I) is not intended to apply to any dwelling receptacles, why doesn’t the NEC explicitly state that?
I’m not trying to stir the pot or play code lawyer—I just want to understand how to apply this properly in the field, especially when going beyond the minimum code requirements.
Thanks in advance for any clarification or citations.
From what I understand, 220.14(J) covers receptacles specifically required by 210.52—namely general-use, small appliance, and laundry receptacles. Those loads are accounted for under the general lighting load using the 3 VA/ft² calculation.
However, optional receptacles—like those in an attic, workshop, bar area, or unfinished basement—aren’t required by 210.52. If that’s the case, wouldn’t they fall back under 220.14(I) and be calculated at 180 VA per yoke?
Some claim that 180 VA never applies in a dwelling, and that all 15A/20A general-use receptacle loads are included in the 3 VA/ft² calc, regardless of location or requirement. But I can’t find a section in the NEC that says 220.14(I) is completely excluded from all dwelling unit receptacles. In fact, 220.14(I) starts with “except as covered in (J),” which suggests it does apply to any receptacle not explicitly covered by (J).
So my questions are:
1. Are there any official references, CMP notes, or Handbook excerpts that clearly explain whether 180 VA per yoke should or should not apply to optional receptacles in dwellings?
2. If 220.14(I) is not intended to apply to any dwelling receptacles, why doesn’t the NEC explicitly state that?
I’m not trying to stir the pot or play code lawyer—I just want to understand how to apply this properly in the field, especially when going beyond the minimum code requirements.
Thanks in advance for any clarification or citations.