Good evening
A new company with different ideas that confuse me.
I'm told to feed a fused disconnect from a 100amp ( 240v) breaker in the msp with 2, 2awg.
Return to the msp with 2, 2awg and connect to the sub panel feeders with Polaris connectors.
All good. From a pv disconnect I will tap to those conductors before the fuses.
But they also want a 2awg in and out of the neutral bar of the disconnect from the msp.
I would think I could just pass the #8 neutral of the inverter output through the disconnect straight to the msp neutral bar.
This would satisfy the conditions of 215.a(2) and table 250.122.
This would allow me to pull 4 #2s and 2 #8s , one neutral, one egc rather than 6 #2s and 2 #8s .
Am I right or wrong.?
Sorry for the length of the question. But I appreciate any answers.