Hi all,
We are looking at a single POCO connection at 208Y/120V 3-ph 4w for what is basically 2 residential units and an attached workshop.
For the 2 residences I was able to get the load using part III and part IV calculation.
For the workshop, I am understanding that I follow:
Table 220.42 for lighting loads
Article 430 for motors
Article 630 for arc welders
I'd like to confirm that there are no demand factors applied to these connected loads in the workshop except as outlined in the specific articles in 430 and 630?
Thanks much!