Per NEC 725.48(B)(1), class 1 circuits and power circuits shall be permitted to occupy the same cable or raceway, only where the equipment powered is functionally associated. Per NEC 725.49(B), the insulation on the class 1 circuit shall be the same of the power circuit insulation -this corresponds with NEC 300.3(C)(1).
If a proposed installation requires 1000V rated power circuit, and the class 1 circuit can only be procured with a 600V rating, could installing the class 1 circuit in innerduct, within the same raceway as the power circuits, meet NEC intent? My understanding is NO, unless there was an innerduct out there with a 1000V rating. The electrical noise/interference from the 1000V rated power circuit may have an adverse affect on the 600V class 1 circuit.
Thoughts? Any ideas on how to mitigate this? Installing the power and comms in separate conduit is not a viable solution. Procuring 1000V rated comms is also not a viable solution.
Thanks
If a proposed installation requires 1000V rated power circuit, and the class 1 circuit can only be procured with a 600V rating, could installing the class 1 circuit in innerduct, within the same raceway as the power circuits, meet NEC intent? My understanding is NO, unless there was an innerduct out there with a 1000V rating. The electrical noise/interference from the 1000V rated power circuit may have an adverse affect on the 600V class 1 circuit.