Can a Class 1 Div 2 cable (PLTC or TC) with a gas impervious polymer jacket run through a Class 1 Div 1 location if the cable is not terminated in the Div 1 area? Cable is terminated outside the Class 1 Div 1 area. Where in NEC would that be described?
 
Can a Class 1 Div 2 cable (PLTC or TC) with a gas impervious polymer jacket run through a Class 1 Div 1 location if the cable is not terminated in the Div 1 area?
No.

Cable is terminated outside the Class 1 Div 1 area. Where in NEC would that be described?
Section 501.10(A) defines what is permitted, anything else is prohibited.
 