Class 1 Div 1 Conduit requirements.

Status
Not open for further replies.
We are building a piece of equipment to be used in a class 1 Div 1 location. I am somewhat confused by what exactly is required to run conduit between a terminal box on the back and a bank of 6 solenoid switches on the side of the equipment. I had planned to run conduit and then short runs of sealtite from tee's to the solenoids. I believe 18" or less is allowed. If anyone can point me to where I can find more information on the requirements of running explosion proof conduit I'd greatly appreciate it.

Premade lengths of MI cable works real well for these type installations, yet not used too often. It provides you with the most trouble free installation. Coil the extra lengths of cable at the device end.

http://www.micable.com/
 