I’m in a situation where I went to a job that was already started and tasked with completing the small project.
I have a 2”conduit that stubs up into a class1 division 2 area. Full Pvc coated rigid. (Rob roy).
Problem is where the conduit stubs up it is a stub 90degree coming out of the ground with a nipple.
Problem with that is the coupling is above grade and obviously need the boundary seal off first. I can’t just take the nipple out and replace with a seal because it would be partially in the stone (frowned upon and looks bad).
So we was going to completely dig up and replace but it’s in a very bad area to get to dig up to be able to spin the stub off and replace with a longer one that emerges from grade with no coupling before the seal..
So after digging a while we discovered we could in a sense undermine the conduit and get it to go lower putting the coupling below the stone, and having the boundary seal the first fitting in the area.
I’ve gotten this approved by the company’s engineer, I was just curious as to if there was any other regulations on this. I have read over for boundary seals and have not seen anything regarding the conduit must be continuous for such length before emerging from grade and interning the seal. Just that the seal must be the first out of the ground with no couplings or fittings between the seal and grade.
I have a 2”conduit that stubs up into a class1 division 2 area. Full Pvc coated rigid. (Rob roy).
Problem is where the conduit stubs up it is a stub 90degree coming out of the ground with a nipple.
Problem with that is the coupling is above grade and obviously need the boundary seal off first. I can’t just take the nipple out and replace with a seal because it would be partially in the stone (frowned upon and looks bad).
So we was going to completely dig up and replace but it’s in a very bad area to get to dig up to be able to spin the stub off and replace with a longer one that emerges from grade with no coupling before the seal..
So after digging a while we discovered we could in a sense undermine the conduit and get it to go lower putting the coupling below the stone, and having the boundary seal the first fitting in the area.
I’ve gotten this approved by the company’s engineer, I was just curious as to if there was any other regulations on this. I have read over for boundary seals and have not seen anything regarding the conduit must be continuous for such length before emerging from grade and interning the seal. Just that the seal must be the first out of the ground with no couplings or fittings between the seal and grade.