Class 1 Div 2 Boxes

Status
Not open for further replies.

jbolen

Senior Member
What type of enclosure are required to be used as junction boxes only in Class 1 Div 2.

Additionally what are restrictions on the use of liquid-tight flexible metal if any in Class 1 Div 2.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
  • Boxes and Fittings: see Section 501.10(B)(4). They don't necessarily have to be explosionproof but still need to be appropriate for the "weather".
  • LFMC: see Sections 501.10(B)(2) and 501.30, especially 501.30(B).
 