Excuse my Article 500 ignorance, but I need a sanity check. I can't find where the code lists acceptable juction boxes for a Class 1 Div 2 area.
Per 501.10(B)(4) Boxes and Fittings "Boxes and fittings shall not be required to be explosionproof except as required by 501.105(B)(1), 501.115(B)(1) and 501.150(B)(1)
Per 500.8(A)(3) Where specifically permitted in Articles 501 through 503, general-prpose equpment or equipment in general purpose enclosures shall be permitted to be installed in Division 2 locations if the equipment does not constitute s source of ignition under normal operating conditions."
Does allow for the use of a 4 square box for a pulling or junction box as long as it doesn't contail any arcing devices or devices that may cause ignitian by surface temperature? The commentary imediately following 510.10(B)(4), mentions "Where general purose enclosures and permitted...", but I can't seem to find a definition of "general purpose enclosure". I've looked the forum and noticed the reference to nema 4 and 4x multilple times for C1D2 areas, but can't find a reference in the code at all. Can someone refer me to where the code may list acceptable enclosures for Class 1 Div 2 that will be used for pulling and possibly splicing of branch circuits (any arcing device will be in explosion proof enclosures with approprate sealing). I have a hard time envisioning using rigid conduit and a 4 square box.
Per 501.10(B)(4) Boxes and Fittings "Boxes and fittings shall not be required to be explosionproof except as required by 501.105(B)(1), 501.115(B)(1) and 501.150(B)(1)
Per 500.8(A)(3) Where specifically permitted in Articles 501 through 503, general-prpose equpment or equipment in general purpose enclosures shall be permitted to be installed in Division 2 locations if the equipment does not constitute s source of ignition under normal operating conditions."
Does allow for the use of a 4 square box for a pulling or junction box as long as it doesn't contail any arcing devices or devices that may cause ignitian by surface temperature? The commentary imediately following 510.10(B)(4), mentions "Where general purose enclosures and permitted...", but I can't seem to find a definition of "general purpose enclosure". I've looked the forum and noticed the reference to nema 4 and 4x multilple times for C1D2 areas, but can't find a reference in the code at all. Can someone refer me to where the code may list acceptable enclosures for Class 1 Div 2 that will be used for pulling and possibly splicing of branch circuits (any arcing device will be in explosion proof enclosures with approprate sealing). I have a hard time envisioning using rigid conduit and a 4 square box.