We have a upcoming project that is listed on the prints as a Class 1 Div 2 environment ......

My understanding of the code is

1) I need a seal off within the first 18 inches of conduit from the device

and

2) A seal off directly after I exit the Class 1 div 2 environment...

My question is if I have a devise located on the wall off the booth can I pass directly thru the booth wall and install a seal off and only use one?

Thanks in advance
 
We have a upcoming project that is listed on the prints as a Class 1 Div 2 environment ......

My understanding of the code is

1) I need a seal off within the first 18 inches of conduit from the device

and

2) A seal off directly after I exit the Class 1 div 2 environment...

My question is if I have a devise located on the wall off the booth can I pass directly thru the booth wall and install a seal off and only use one?

Thanks in advance

IMHO... no... the purpose of the seal is to isolate the atmosphere within the conduit before you get to the device....
 
Note the device would require a seal within 18" only if the conduit is entering an enclosure required to be explosionproof.

I would think a single seal fitting would be acceptable provided the seal was within 18" of the device, was within 10 ft of the Cl I Div 2 boundary, and there were no other fittings between the seal and the boundary, per 501.15(B)(2).
 
My first question would be how the interior of the booth was only classified Division 2. [Sections 516.3(B)(1) and 516.3(C)(4)]
 