angrymonkey
We have a Class-1 Div-2 hazardous location with armor-clad cables feeding 277v circuits
into the classified area. The contractor installed seals on the ends of each feeder cable
landing them into JIC hinged gasketed 4X enclosure. The contractor used terminal strips
inside the junction box to splice wires going to each load in the hazardous area.
Each of the cables leaving the JIC junction/splice box has a seal as it leaves the j-box.
Contractor is claiming the application is non-arching & sparking and does not need
to be installed in an enclosure rated for the area.
I see several problems with this installation:
The enclosure is not UL listed for the application (4X enclosure)
The wires are spliced inside the junction box (gas can migrate past the seals inside the wires)
The enclosure will not contain the explosion if the gases ignite inside the j-box.
The enclosure gasketed seal will not cool the escaping gases to a safe temp in the hazardous
area if the gases inside the enclosure ignite and escape.
Anyone have an opinion be on this?