bman

Member
Just trying to figure out if a battery storage/charging room is considered a hazardous location. I plan on installinng lights and plugs as well as an exhaust fan which I believe will remove the hazardous conditions (I.E. hydrogen gas from charging), if this will work, does the fan itself have to be rated for hazardous locations?...
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: Class 1 div 2

Battery rooms installed in compliance with Article 480 are not required to be classified.
 