Class 1, Div 2

Status
Not open for further replies.

twoelk

Member
Location
USA, West Coast
I am running pvc coated rigid from the overhead cable tray, outside of the classified area, to a transmitter in the class 1, div 2 area. I am going to use liquid tight flex at the transmitter, do I need to do anything other than bonding on the tray end?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
See Section 501.15(B)(2) and its Exception 2. Read both the main rule and the Exception carefully.
 

bobgorno

Senior Member
Location
Colorado
And for the cable inside, 501.15(E), and for your device connected to the process 501.15 (F), look for dual seal.

Remove the cable jacket, but not the shield....

Look at 501.30(B), exception for your EGC. Make sure the LFMC fittings are listed for grounding.
 