Class 1. Division 1

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The wiring method in the classified area must be one of the wiring methods in 501.10(A). While 501.10(A)(2) permits flexible cord for applications where flexiblity is required, I doubt that would apply here. Also don't forget the seal fitting that will be required in the wiring method between the classified and non-classified areas. 501.15(A).
 
Location
Brownstown Michigan
Occupation
Electrician
The wiring method in the classified area must be one of the wiring methods in 501.10(A). While 501.10(A)(2) permits flexible cord for applications where flexiblity is required, I doubt that would apply here. Also don't forget the seal fitting that will be required in the wiring method between the classified and non-classified areas. 501.15(A).
We want it to be safe, so metal conduit and seal fittings it will be according to art. 501. Thank You!
 