Jon Reuter
Member
- Location
- Murrieta, CA, USA
Article 501.10.b.4 States that Boxes and fittings don't need to be rated Explosion-Proof (except as required...). I read this as being able to use standard threaded conduit bodies (LBs, Tees, Condulets...) in a Class 1 Division 2 area. I am retrofitting a building to Cl1 Div2 and the conduit system feeding the existing lighting is RMC with Threaded Steel Fittings. I don't want to have to replace them with Cl1 Div1 Fittings. Am I reading this section correctly? I know that I have to replace the Light Fixtures and provide Seals at those locations.