I will be contacting the AHJ regarding this question. I have a panel that is 72" high. in order to have it outside the 30" boundary The top breakers would exceed the 6'7" maximum height for installation. My question is this. Is the boundary based on the height of the back box or is it based on where the lowest breaker would be? If the back box was mounted at 27-1/2" I would be within the 6'7" height restriction. The main breaker would be at 38" above finished floor which is where I would assume any arching could ocurr. Any thoughts?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
First, let's talk about the '30" boundary'. Where did that come from? In general, with no ventilation, the classified location envelope is 18" above the floor.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It would be my opinion that 511.7(B)(1)(a) would prohibit the enclosure from being in the classified area.
What is the code reference for the 30" boundary?
 