Do Article 725 Class 1 requirements apply to DC circuits? Seems like it does to me.
But I have a vendor supplying 24VDC 2A actuators that are supplied with a 5 ft pigtail and no provisions to terminate conduit to the housing. The controller for the actuators has a max capacity of 10A. (240VA) They recommend connecting the pigtail to the building wiring at a j-box, with a terminal strip or wire nuts to facilitate removal for repair.
Seems like this wiring should be in conduit for the entire run. What do you think?
But I have a vendor supplying 24VDC 2A actuators that are supplied with a 5 ft pigtail and no provisions to terminate conduit to the housing. The controller for the actuators has a max capacity of 10A. (240VA) They recommend connecting the pigtail to the building wiring at a j-box, with a terminal strip or wire nuts to facilitate removal for repair.