I have been using the NEC for 20 some years now, but cannot find substantiation for what I believe to be a very typical requirement (and industry standard practice). I might be missing the forest for the trees.
Where (in NEC, UL, IBC) does it require that below 600 volts, electric light and power wiring or class 1 conductors (typically all THWN / THHN wire types ) must be in conduit? I am referring to 90% of all power wiring in a commercial building. I see where the NEC refers to ?when subject to physical damage?, but what about above drywall ceilings, or in block walls, ect.?
If someone can quote this requirement, in and of itself, my next question is already answered. If not... read on.
I have a situation where a contractor has run exposed conductors of common TFFN / THHN to serve a class 2 low voltage circuit, and in a non-environmental plenum to boot.
I have even talked to engineers at wire manufacturers and they cannot put their finger on where the NEC requires conduit for conductors like this. They also do not believe that the UL listing of the wire requires use of a raceway (but they are not positive). I could see that with certain flame ratings, the installation of the wire could be restricted to some type of raceway.
I know that division 16 is typically specified to have everything in conduit with exceptions for class 2, but that isn't code, just industry practice.
Any thoughts?
UUGGGHHH...
Where (in NEC, UL, IBC) does it require that below 600 volts, electric light and power wiring or class 1 conductors (typically all THWN / THHN wire types ) must be in conduit? I am referring to 90% of all power wiring in a commercial building. I see where the NEC refers to ?when subject to physical damage?, but what about above drywall ceilings, or in block walls, ect.?
If someone can quote this requirement, in and of itself, my next question is already answered. If not... read on.
I have a situation where a contractor has run exposed conductors of common TFFN / THHN to serve a class 2 low voltage circuit, and in a non-environmental plenum to boot.
I have even talked to engineers at wire manufacturers and they cannot put their finger on where the NEC requires conduit for conductors like this. They also do not believe that the UL listing of the wire requires use of a raceway (but they are not positive). I could see that with certain flame ratings, the installation of the wire could be restricted to some type of raceway.
I know that division 16 is typically specified to have everything in conduit with exceptions for class 2, but that isn't code, just industry practice.
Any thoughts?