Based on the NEC language below, it seems I can put a typical Cat6 cable in a wireway with power THHN conductors. I say this because a Cat6 cable meets the definition of a nonmetallic-sheathed cable: "A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket."
That said, my interpretation feels wrong. I would love to hear your thoughts on if you think the NEC allows this.
From 725.136(I)1 2023 NEC:
"Conductors of Class 2 circuits shall be separated by at least (2 in.) from conductors of any electric light, power, Class 1, non-power-limited fire alarm, or medium-power network-powered broadband communications circuits unless one of the following conditions is met:
(1) Either all of the electric light, power, Class 1, non-power-limited fire alarm, and medium-power network-powered broadband communications circuit conductors or all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, nonmetallic-sheathed, Type TC, or Type UF cables."
That said, my interpretation feels wrong. I would love to hear your thoughts on if you think the NEC allows this.
From 725.136(I)1 2023 NEC:
"Conductors of Class 2 circuits shall be separated by at least (2 in.) from conductors of any electric light, power, Class 1, non-power-limited fire alarm, or medium-power network-powered broadband communications circuits unless one of the following conditions is met:
(1) Either all of the electric light, power, Class 1, non-power-limited fire alarm, and medium-power network-powered broadband communications circuit conductors or all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, nonmetallic-sheathed, Type TC, or Type UF cables."