Wacokidd63
Member
- Location
- Ohio
- Occupation
- Inspector
Was wanting to get an opinion if this met article 725.136(D).
Found a class 2 transformer in a 4 gang box with switches and lighting power circuits. It is grounded and separated from the power and switches by more than a .25” as the code requires and the class 2 cable is only in the box to connect to the transformer but I’m still skeptical. The transformer is thermally protected and seems to be completely fine where it is.
Obviously this is not ideal or good electrical work in my opinion but I’m curious if it would meet this section of the code. I’ve seen these transformers installed like this before and cannot figure out how they pass inspection.
Found a class 2 transformer in a 4 gang box with switches and lighting power circuits. It is grounded and separated from the power and switches by more than a .25” as the code requires and the class 2 cable is only in the box to connect to the transformer but I’m still skeptical. The transformer is thermally protected and seems to be completely fine where it is.
Obviously this is not ideal or good electrical work in my opinion but I’m curious if it would meet this section of the code. I’ve seen these transformers installed like this before and cannot figure out how they pass inspection.